10 hours ago, JNock said:600-800 watt it’s around 80
...must be balanced between L1 / L2, or more on the L2 circuit. If it was entirely on the L1 circuit, I'd expect ~250 counts.
10 hours ago, JNock said:Ac pass through is 25
That'd be the problem ;-). That's what I get for putting filter caps on the wrong side of the hall sensor, as it should be zero...or slightly negative. Threshold for safety error is +45 counts; looks like I should increase that threshold a bit so it stops tripping.
This number will go negative in grid-tie backfeed and/or normal battery charge conditions.
10 hours ago, JNock said:it won’t charge because the batteries are at 51v since I got 15kwh of solar today
That's always the best 😉.
10 minutes ago, Sid Genetry Solar said:...must be balanced between L1 / L2, or more on the L2 circuit. If it was entirely on the L1 circuit, I'd expect ~250 counts.
That'd be the problem ;-). That's what I get for putting filter caps on the wrong side of the hall sensor, as it should be zero...or slightly negative. Threshold for safety error is +45 counts; looks like I should increase that threshold a bit so it stops tripping.
This number will go negative in grid-tie backfeed and/or normal battery charge conditions.
That's always the best 😉.
Last night when I used the pressure cooker I had to restart it and the code was transformer volt
Last night when I used the pressure cooker I had to restart it and the code was transformer volt
Pass-thru grid powered I assume?