For the neutral/earth link part unless you had grid AC wired to the inverter's AC inputs there's little you could do that would result in an instant blow up apart from managing to short L1 to L2 or L1 to neutral or L2 to neutral.  Even if your PJ had an internal neutral/earth link for some reason that shouldn't result in a blow up if you also did that externally (again assuming nothing on the inverters AC input).

There are people here that persist in using these things, so perhaps one of them can offer some better explanation of why your inverter decided to go foom.


   
ReplyQuote
(@dickson)
Noble Member
Joined: 4 years ago
Posts: 1058
 

Even if your PJ had an internal neutral/earth link for some reason that shouldn't result in a blow up if you also did that externally (again assuming nothing on the inverters AC input).

There are people here that persist in using these things, so perhaps one of them can offer some better explanation of why your inverter decided to go  BOOM .   

IF your inverter is a Powerjack then  in the USA  it is always a   floating neutral  and  NOT an internal neutral/earth link .    The  connection  of inverter in a RV  is not the same  if you  connect to  shore  power  as the  RV  do not have  a  ground  where shore power  has the ground and neutral  connected to a ground  rod at one and only one spot .     It  would help if you took pictures of  your  connection  to the  breaker and ground .        Unless you had grid AC wired to the inverter's AC inputs there's little you could do that would result in an instant blow up  on first power up .        Sean in youtube  managing to short L1 to L2 or L1 to neutral or L2 to neutral  on the GS 12kw and  did  not  do any damage  .   I  did the same as what Sean  did to my  PJ  three years ago and  do no damage but  sound like a shotgun  blast .    


   
ReplyQuote
(@dickson)
Noble Member
Joined: 4 years ago
Posts: 1058
 

 I fried an inverter. I think. And, I had it replaced by Amazon- and still have not returned the old one. Of course, i never received the replacement, but I have 14 days left to return this and I want to figure this out first so I can decide if it's worth buying another. 

Return  this inverter  if Amazon will give you a free replacement  .     If this is a Powerjack inverter  then  it should have  a   120 vac oullet  in front of the case  .     There is nothing  to figure out  .     Just plug  a  night light when you get the replacement inverter  and  it will  work when switch on .     The only connection  is the 12v  positive cable and the 12v  negative   cable  .     GROUND  Connection  is not necessary  to test  .      For RV or Boat   permanent connection  you need  GFCI   receptacle  to be safe .   


   
ReplyQuote
pilgrimvalley
(@pilgrimvalley)
Prominent Member
Joined: 4 years ago
Posts: 826
Topic starter  
Posted by: @dickson
This youtube video show improper bonding by the user . Could this cause a liabilty problem for GS inverter and the user is electrocuted by miss-wiring ??

the video was not there??? did they block it???


   
ReplyQuote
(@thebutcher)
Reputable Member
Joined: 4 years ago
Posts: 355
 

Yep, gone private.  I guess he took too much flack for not really understanding what was going on or possibly that Youtube's stupid classification system decided that he was encouraging dangerous activity in minors, because he demonstrated that sticking a wire into the ground would pass current.

You aren't missing much.  Essentially he 'discovered' that you could pass current from a live wire, through an appliance, and to earth and run that appliance if it wasn't particularly current hungry nor voltage sensitive.  It's a perfectly normal situation when there is a local neutral/earth join and earth stake (or equiv of).  His GFCI tripped when he tried a higher load because it exceeded the trip current of the GCFI, something that really should have told him exactly what was going on.


   
ReplyQuote
(@inphase)
Estimable Member
Joined: 4 years ago
Posts: 159
 

This neutral/ground bonding thing is too much. I've spent 25 years on job sites, engineering offices, and the internet trying to explain it, and people just blink and keep on talking about a rod in the dirt. If you don't understand how electricity works, it will forever remain a mystery, I'm afraid.


   
ReplyQuote
(@dickson)
Noble Member
Joined: 4 years ago
Posts: 1058
 

the video was not there??? did they block it???

 If you don't understand how electricity works, it will forever remain a mystery, I'm afraid.  

Yep, gone private.  I guess he took too much flack for not really understanding what was going on or possibly that Youtube's stupid classification system decided that he was encouraging dangerous activity

That  is the guy  who  live a few miles from me  !!!!!           Too  many  people  like that  including  engineers  who  think  solar  inverter are too dangerous  and  only be  use for  camping   off-grid    and never be connected  L1  N  L2   to power   a  house  .      

 


   
ReplyQuote
(@carlos-garcia)
New Member
Joined: 2 years ago
Posts: 1
 
On 7/10/2021 at 12:17 PM, pilgrimvalley said:

our ac output as follows: 

2 ac output socket, output is 110v, also we have hard wire terminal-----L1, N, L2,

L1+L2=220V, L1+N=110V, L2+N=110V  

Note: can not L1+N+L2 at the same time!!!

 

  • 15000W Low Frequency Split Phase 

  • Pure Sine Wave Power Inverter 

  • DC 24V   AC 110V,220V 60HZ

    • With UPS & ATS

    • With 110V Battery Charger

    • With 110V & 220V LCD Display Box

  • AC 110V: 7500W continue power, 30000w peak power

    AC 220V: 7500W continue power, 30000w peak power

    • We separte the control board and the transfomer in two boxes,

    • so cusotmer will receive two boxes as photos show,

      one is the transformer box,the other is the control box

I purchased a 15000 watt just recently, installed it was working fine until I decided to use 240 vac. Didn't realize you must use a external device in order to use 240 so I guess I messed something. Have a question....I purchased it in USA and brought it to Guatemala...now I need to purchase parts and I don't know what needs to be replaced, and do you ship to Guatemala.... Gratefully   Carlos Garcia.

 

On 7/10/2021 at 12:17 PM, pilgrimvalley said:

our ac output as follows: 

2 ac output socket, output is 110v, also we have hard wire terminal-----L1, N, L2,

L1+L2=220V, L1+N=110V, L2+N=110V  

Note: can not L1+N+L2 at the same time!!!

 

  • 15000W Low Frequency Split Phase 

  • Pure Sine Wave Power Inverter 

  • DC 24V   AC 110V,220V 60HZ

    • With UPS & ATS

    • With 110V Battery Charger

    • With 110V & 220V LCD Display Box

  • AC 110V: 7500W continue power, 30000w peak power

    AC 220V: 7500W continue power, 30000w peak power

    • We separte the control board and the transfomer in two boxes,

    • so cusotmer will receive two boxes as photos show,

      one is the transformer box,the other is the control box

 


   
ReplyQuote
(@sid-genetry-solar)
Member Admin
Joined: 4 years ago
Posts: 2890
 
1 hour ago, Carlos Garcia said:

I purchased a 15000 watt just recently, installed it was working fine until I decided to use 240 vac. Didn't realize you must use a external device in order to use 240 so I guess I messed something. Have a question....I purchased it in USA and brought it to Guatemala...now I need to purchase parts and I don't know what needs to be replaced, and do you ship to Guatemala.... Gratefully   Carlos Garcia.

Well, it's worth noting that *any* AC input on a PJ inverter is liable to cause failure.  Case in point: it should have rejected the 240v input and not switched over!

Genetry Solar has not been an "authorized PJ repair center" for over a year now--we do not have official replacement parts nor manufacturer authorization any more.  Your best bet for replacement parts would be to contact the original seller you purchased the inverter from.


   
ReplyQuote
(@robertm)
Estimable Member
Joined: 3 years ago
Posts: 205
 
Posted by: @carlos-garcia
I purchased a 15000 watt just recently, installed it was working fine until I decided to use 240 vac. Didn't realize you must use a external device in order to use 240 so I guess I messed something. Have a question....I purchased it in USA and brought it to Guatemala...now I need to purchase parts and I don't know what needs to be replaced, and do you ship to Guatemala.... Gratefully Carlos Garcia.

The external device is the "power choke"?


   
ReplyQuote
(@lener)
Trusted Member
Joined: 2 years ago
Posts: 44
 
On 1/12/2023 at 8:39 PM, Sid Genetry Solar said:

Well, it's worth noting that *any* AC input on a PJ inverter is liable to cause failure.  Case in point: it should have rejected the 240v input and not switched over!

Genetry Solar has not been an "authorized PJ repair center" for over a year now--we do not have official replacement parts nor manufacturer authorization any more.  Your best bet for replacement parts would be to contact the original seller you purchased the inverter from.

I wish I had known ( worth noting that *any* AC input on a PJ inverter is liable to cause failure.) I have wasted a lots of my time trying to figure out why the  New AGM 12000w PJ tripping the input breaker…….. isn’t the the whole purpose of the input is to function as ATS and charger ( all useless options) I  have wasted $649 on a complete piece of junk and yeah after the transaction  complete silent from Jely or jack. ( Superpower) I bought an other Powmr , very simple installation  and working without tripping any of breakers.

<a href="/monthly_2023_01/image.jpg.9bb7003e079c55a4cea6f9fd17c68f43.jpg" class="ipsAttachLink ipsAttachLink_image" ><img data-fileid="2089" src="//forums.genetrysolar.com/applications/core/interface/js/spacer.png" data-src="/monthly_2023_01/image.thumb.jpg.bef80ee826ed0df5808ac2e96019a5c6.jpg" data-ratio="75" width="1000" class="ipsImage ipsImage_thumbnailed" alt="image.jpg">


   
ReplyQuote
(@sid-genetry-solar)
Member Admin
Joined: 4 years ago
Posts: 2890
 
Posted by: @lener
I bought an other Powmr , very simple installation and working without tripping any of breakers.

Worth noting that the PowMr and other similar units are all HF-based inverters.  If they work for your needs...great 👍

But they are often between not-so-good and just plain terrible with surge loads (well pumps, etc.)  Not to mention being basically impossible to repair by the end user (if necessary).


   
ReplyQuote
(@lener)
Trusted Member
Joined: 2 years ago
Posts: 44
 
Posted by: @sid-genetry-solar
Well, it's worth noting that *any* AC input on a PJ inverter is liable to cause failure. Case in point: it should have rejected the 240v input and not switched over!

I wish I had known ( worth noting that *any* AC input on a PJ inverter is liable to cause failure.) I have wasted a lots of my time trying to figure out why the  New AGM 12000w PJ tripping the input breaker…….. isn’t the the whole purpose of the input is to function as ATS and charger ( all useless options) I  have wasted $649 on a complete piece of junk and yeah after the transaction  complete silent from Jely or jack. ( Superpower) I bought an other Powmr , very simple installation  and working without tripping any of breakers.


   
ReplyQuote
(@lener)
Trusted Member
Joined: 2 years ago
Posts: 44
 

Does anyone know   About this adjustment potentiometer/ battery adjustment. It just goes around and around does not seem to do anything nor that can tell .now After I touched  it of course the ATS does not engage anyone longer..

Thanks.

FF259305-A5D2-45B8-9642-ED53D7072D9A.jpeg


   
ReplyQuote
(@sid-genetry-solar)
Member Admin
Joined: 4 years ago
Posts: 2890
 
10 hours ago, Lener said:

Does anyone know   About this adjustment potentiometer/ battery adjustment. It just goes around and around does not seem to do anything nor that can tell .now After I touched  it of course the ATS does not engage anyone longer..

Thanks.

//content.invisioncic.com/g308908/monthly_2023_01/FF259305-A5D2-45B8-9642-ED53D7072D9A.thumb.jpeg.243c579cda43326914d07015bf77e8c1.jpeg

So that is a 10-position switch that selects between predefined battery charge settings (should be covered in the manual??)  Several of the settings are "empty", which likely is what's causing ATS not to engage.

Worth noting that several of the "preset battery charge settings" are beyond the OVP (overvoltage protect) thresholds.  Go PJ!


   