yes, Dickson >>>> that was the huge choke i was asking about that PowerJack is selling on eBay.
a bandaid? i have been researching them a bit, but still not ready to try one of those huge expensive chokes.
i do note that when i turn off the heat gun on the 8000-watt PowerJack 24-volt the overhead LED light will flash off as if a shut off surge or flyback issue or something. i am sure i am not using the right word but maybe it needs more capacitors or something , a choke or something to mellow it out when the load is released????
thanks for the replies and pictures.
just about ready to hook up the 15000-watt 24-volt psw sp lf powerjack to the 32 cell LiFePO4 battery build. a few more details. to do to do!!!!!! to do to do!!1😎
i do note that when i turn off the heat gun on the 8000-watt PowerJack 24-volt the overhead LED light will flash off as if a shut off surge or flyback issue or something. i am sure i am not using the right word but maybe it needs more capacitors or something , a choke or something to mellow it out when the load is released????
Betcha it's a firmware voltage regulation reaction...the firmware makes a huge difference in how the inverter handles loads. I'd expect the LED light to briefly "flash" brighter when the heat gun is turned off--though if the LED light has a high line voltage protection, it could conceivably blink "off" for a fraction of a second until the voltage returns to the spec range.
The 4/0 positive cable is 11.0 watts on standby not 0.11 watt . The L2 output is 11.0 watts on the AC side awg 6 cable . This is the new measurement this morning . Last year was 24.0 watts .
What is the make/model of the meter you are using for said measurements?
I didn't say that standby was 0.11 watts; I was referring to the difference between your measurements of the output load ("10.49 watts" on L2) and your measurement of the input load ("10.60 watt" on the battery) is mathematically 10.6 - 10.49 = 0.11 watts loss. In other words, if the transformer is somehow 100% efficient with all the chokes, there is not enough extra power draw on the input to allow operation of the control board.
My point is to prove that the measurement methods are not correct, because the static draw of the control board alone is nearly 2 watts (measured on my bench with a DC power supply, and verified with a Uni-T UT210E DC clamp meter.)
Even assuming the chokes reduced the transformer idle current to nothing (oh happy day!), you will not be able to negate the ~2 watt power draw of the control board.
I personally know a customer who was tweaking things to get extremely low no-load values...only to later find out that their clamp meter was not capable of reading DC amperage, negating all of the tests.
that was the huge choke i was asking about that PowerJack is selling on eBay
I was surprise to see the 490uHenry ferrite choke install on the output AC 120v side . A lightning surge suppressor do have a ferrite choke and a bypass capacitor for the AC 240 v for house surge protection I have one on my house main service 240v to protect the heat pump . A 10uf capacitor on L2 will help start and run inductive load like washing machine and dishwasher . The 490u Henry choke on the DC cable will make a LC circuit for back EMF . Your heat gun cause a huge surge when shut off never happen to me . The Sol Art inverter and Growatt inverter shut down also when there a huge resistive load and willl also shut down when a huge inductive load from a dishwasher and washing machine . This is from youtube review and said the 2 above inverters cause a very dangerous condition because the neutal line is shut off at the same time of the surge but the inverter still output 120v and a person can be electrocuted because the ground is now 120v . That is so confusing that they do not have a solution yet . Need a EE degree to explain all this . This subject is going down a rabbit hole .
I didn't say that standby was 0.11 watts; I was referring to the difference between your measurements of the output load ("10.49 watts" on L2) and your measurement of the input load ("10.60 watt" on the battery) is mathematically 10.6 - 10.49 = 0.11 watts loss
I am confuse about the measurement of output and DC input . I am using the inverter now so I will try to take picture of what I measure tomorrow morning . Thank you .
I didn't say that standby was 0.11 watts; I was referring to the difference between your measurements of the output load
Surprise a different meter make a big difference . Thank you. DC positive cable 1.434amps at 61.4 v and 0.098 AC amp at 107vac . see picture .
<a href="/monthly_2021_09/DSCF5807.JPG.7b58ee9e7bf67229ca546adbfdf7e7ff.JPG" class="ipsAttachLink ipsAttachLink_image"><img data-fileid="752" src="//forums.genetrysolar.com/applications/core/interface/js/spacer.png" data-src="/monthly_2021_09/DSCF5807.thumb.JPG.4dbd2a605e95def3e222a831f7f91d45.JPG" data-ratio="133.45" width="562" class="ipsImage ipsImage_thumbnailed" alt="DSCF5807.JPG">
<a href="/monthly_2021_09/DSCF5810.JPG.682bebfa9b8096238ecdd492d0ec3712.JPG" class="ipsAttachLink ipsAttachLink_image"><img data-fileid="753" src="//forums.genetrysolar.com/applications/core/interface/js/spacer.png" data-src="/monthly_2021_09/DSCF5810.thumb.JPG.b8c29b74e0af1f0f4b7f9077954f0589.JPG" data-ratio="133.45" width="562" class="ipsImage ipsImage_thumbnailed" alt="DSCF5810.JPG">
<a href="/monthly_2021_09/DSCF5817.JPG.12659db98f85abe4cecd7e5290771545.JPG" class="ipsAttachLink ipsAttachLink_image"><img data-fileid="754" src="//forums.genetrysolar.com/applications/core/interface/js/spacer.png" data-src="/monthly_2021_09/DSCF5817.thumb.JPG.cd347c631f1631eee82c643e2c1b908d.JPG" data-ratio="75" width="1000" class="ipsImage ipsImage_thumbnailed" alt="DSCF5817.JPG">
<a href="/monthly_2021_09/DSCF5819.JPG.58675b78135f0273b35b74de0c6fdacc.JPG" class="ipsAttachLink ipsAttachLink_image"><img data-fileid="755" src="//forums.genetrysolar.com/applications/core/interface/js/spacer.png" data-src="/monthly_2021_09/DSCF5819.thumb.JPG.fb5d24b677a28d28222cb3d0c681730b.JPG" data-ratio="75" width="1000" class="ipsImage ipsImage_thumbnailed" alt="DSCF5819.JPG">
Surprise a different meter make a big difference . Thank you. DC positive cable 1.434amps at 61.4 v and 0.098 AC amp at 107vac . see picture .
Bingo, there we go....
So now when measuring DC amps, you need to set the Uni-T UT210E to DC amp scale. To do this, set it to the desired range (in your case 2A). Then press the blue button. Note the LCD display will switch from "AC" to "DC". Press the black button ("Zero"). Meter should drop to near zero. NOW you can clamp it to the battery DC wire.
Note that every time you change the amp scale (2A / 20A / 100A), the meter will revert back to AC amps; you will have to re-set it to DC amps, and re-zero it. Make sure that you remove the meter from the wire when zeroing, otherwise it will "zero" whatever the current load is.
1.434A @ 61v on the battery is pretty high for no load.......ideal should be under 1A.
@dicksonBTW the MT87 meter is NOT designed to measure DC amps.
1.434A @ 61v on the battery is pretty high for no load.......ideal should be under 1A.
I was using the wrong meter before amd now measure the positive cable again with Uni-T UT210E and reading 1.6amps at 57 vDC . This is still high so the choke on the positive cable outside the inverter probably not lower the standby current and maybe increase the current . The choke inside the box on the primary of transformer do lower the standby current . Thank you .
This is still high so the choke on the positive cable outside the inverter probably not lower the standby current and maybe increase the current .
I doubt it is doing anything. It may reduce AC ripple on the lines (as indicated by reduced AC amperage readings), but it won't significantly help anything else. I don't think it'll increase the current at all.
The choke inside the box on the primary of transformer do lower the standby current
2 full turns around the PJ choke (if at all possible) on the low voltage side of the transformer (primary side) will give you the best result. (I don't expect much of any change with a choke on the high voltage side--secondary--of the transformer.)
And yes, I try to specify "primary" and "secondary" simply because PJ seems to label the low voltage side as the "O.P" (output) and the high voltage side as the "I.P." (input). Doesn't make sense to me, but keeping the vernacular clear should help prevent confusion...
If your system regularly runs >60v, you'll probably benefit quite a bit from a second low-side choke on the transformer. The higher the difference between the transformer spec voltage and the actual battery voltage, the more chokes will be necessary to keep the no-load current down. One on each side of the primary winding should have the best results.
If your system regularly runs >60v, you'll probably benefit quite a bit from a second low-side choke on the transformer.
Yes I added a second choke on the other primary of the transformer from what you tested on this forum eariler . The best improvment was removing one complete main board . Blow up 48 FETs is too expensive . 24 FETs on ebay is now over 100 dollars and 30 dollars for LF driver .
1.434A @ 61v on the battery is pretty high for no load.......ideal should be under 1A.
I watch Sean youtube about how he measure standby ampage . The PJ 6000 watt inverter measure 0.10 amp which is 1.35 watt with the switch OFF . My mistake was measuring 1.6amps with the switch ON and the fan ON . Now measure again with switch off and fan off is 0.42amp at 57vDC is now the same as last year 24 watts . Thank you Sid for your patience to answer my stupid mistake . The choke by PJ on ebay probably do nothing but cost over 100 dollars .
15,000 watt 24-volt 3 piece PowerJack inverter : big spark trying to install class t fuse?? it was one of my final connections. ... so had to stop and rethink....
Question#1 : Was this because the inverter had already been hooked up to another 24-volt lifepo4 battery (for testing) and the capacitors were already charged up? when i turned the inverter on without power then the green led went down to off.
Question#2: So is it now with the capacitors discharged? are the capacitors now discharged?
Sorry for the dumb questions, but I am still learning and a bit cautious!
as this is a 1088Ah battery .... I decided to add the BlueSea battery switch ... I am putting it on the negative side of the battery....
it is only rated at 350 amps 48 volts continual.
thanks in advance for any help/suggestions! 😎
Was this because the inverter had already been hooked up to another 24-volt lifepo4 battery (for testing) and the capacitors were already charged up?
Are you trying to parallel the 1088ah battery to the 24 v lifepo4 battery already connected ? Need to check the voltage of the 2 different battery bank before parallel the connection . The voltage of 2 different battery bank should be the same within 2 volts . There will be a huge spark becuase the 2 bank of battery will equalize in millisecond .
If the capacitor is discharge when all cables is disconnected then do you know how to pre-charge the capacitor to avoid a huge spark when the inverter switch turn on to charge the capacitor in millisecond ?
Sorry to ask a question to your question .
15,000 watt 24-volt 3 piece PowerJack inverter : big spark trying to install class t fuse?? it was one of my final connections. ... so had to stop and rethink....
If it was wired up forwards, then in all likelihood this is normal expected behavior.
Like @dickson reminded, using a light bulb or other resistive load to "precharge" the inverter (to avoid the surge) is always a good idea; the surge of those main filter caps is insane. (I personally have had the surge damage other DC devices connected to the battery bank due to overvoltage.)