Just got my new PJ LFPSW-8000 Inverter

94 Posts
8 Users
0 Likes
1,377 Views
 Paul
(@paul)
Trusted Member
Joined: 3 years ago
Posts: 55
 
Posted by: @dickson
You are not off topic . The new AMG with 6 wires transformer with 2 secondary 120v windings is better for single phase 120vac . Your 8 kw 230 vac single phase 50 hz produce more output than the AMG wired as split phase L1 N L2 . The AMG should only be wire L1 and L2 and Ground for 240vac 60 hz single phase OR 120vac single phase . The old 5 wires transformer has one secondary winding and a center tap is good for split phase L1 N L2 . AMG is not recommended for L1 N L2 .

Ah thanks for the explanation, it makes sense now. I've never quite got my head around the US split-phase system. In the UK and most of Europe domestic supplies are usually single phase 230v, industrial supplies usually 3-phase.


   
ReplyQuote
(@dickson)
Noble Member
Joined: 4 years ago
Posts: 1058
 

Ah thanks for the explanation, it makes sense now.

Your welcome .   The old  5 wires transformer has  the one secondary as a 240vac winding  and the center tap makes two 120vac  secondary  for L1  N  L2 .   The AMG has 2 separate  secondary windings and both are 120vac  so not good for L1  N  L2  .    PJ in China do not understand  240vac split phase  and advertise the AMG as having  more output but  actually output less with the rev 11.1  control board .    

 


   
ReplyQuote
(@sid-genetry-solar)
Member Admin
Joined: 4 years ago
Posts: 2890
 
Posted by: @dickson
AMG is not recommended for L1 N L2 .

No idea where you get this.

The "AMG" version is based off the GS concept for rewiring the transformer for full output at different voltages.  It is equally at home with a single-phase output, as well as a spit-phase output.  Just rewire it as necessary.

Only difference being that the PJ version only ever regulates 110v from one secondary winding...the other winding is unregulated and appears to also be unfiltered.


   
ReplyQuote
(@sid-genetry-solar)
Member Admin
Joined: 4 years ago
Posts: 2890
 
Posted by: @dickson
The old 5 wires transformer has one secondary winding and a center tap is good for split phase L1 N L2 .

I dunno where you get all this.  There is no internal difference to the transformers, just how the wires are presented.  There is no magic "5-wires" and "6-wires" transformer difference.  The only practical difference is how the wires are presented.

I have a "5-wire" ASL9 PJ transformer.  It still has 2 secondary windings, just the same as the "AMG" transformers.  The only difference on the "5-wires ASL9" is that the "middle" wires of the windings are both crimped into a single lug.  I could literally cut one of the secondary windings' wires out of that lug, crimp them into a separate lug, and *bam* I'd have a "6-wire AMG" transformer.  (Sure, the 2 windings probably won't be balanced voltagewise, but that has nothing to do with the point I'm making here.)

 


   
ReplyQuote
(@sid-genetry-solar)
Member Admin
Joined: 4 years ago
Posts: 2890
 
Posted by: @dickson
The old 5 wires transformer has the one secondary as a 240vac winding and the center tap makes two 120vac secondary for L1 N L2 . The AMG has 2 separate secondary windings and both are 120vac so not good for L1 N L2 .

Again, this is distinction with absolutely no real-world difference.

EVERY SINGLE PJ TRANSFORMER with a split-phase output...has TWO 120v secondary windings, wired in series.  The junction point between the 2 coils is the Neutral line.

If the two windings are put in series inside the transformer...if they're put in series at the crimp lugs on the end of the transformer wires...or if they're put in series externally with an "AMG" jumper wire, it makes NO electrical difference.

 

I've even rewound an older copper-wound PJ transformer (with the colored insulation wires)...and the windings were series-connected internally at the "neutral" junction wire connection.

 

If you unwind a PJ transformer, you'll find all 3 windings (the two 120v windings, and the "DC" side winding) are each separated with a layer of clear plastic wrap.


   
ReplyQuote
(@dickson)
Noble Member
Joined: 4 years ago
Posts: 1058
 

 I could literally cut one of the secondary windings' wires out of that lug, crimp them into a separate lug, and *bam* I'd have a "6-wire AMG" transformer.  (Sure, the 2 windings probably won't be balanced voltagewise, but that has nothing to do with the point I'm making here.)

I  know the point you are  making  that PJ let the buyer decide if the inverter is  120vac single phase  or can be  jumper to be  240vac  single phase  with one 120vac line .  PJ on ebay say  not  L1  N  L2 .   I know it can be wired L1  N  L2  to the house but  the 2 windings  may not be balanced voltagewise .   Is that the reason  PJ  say not L1  N  L2  ?

IF  jumper for  direct  240vac single phase  60 hz  and   L1  and  L2 not balanced  is ok  to start an  inductive load  but if wire split phase  and a large load is on  one of the 120vac line then  the inductive  load   will not get the full 240vac   output  and may not start .   That split phase may have an unbalanced  line  and  reason to not  L1  N  L2  but  wired as L1 and L2  direct to the well pump  without  neutral   and ground  connect to  the  inverter case .  


   
ReplyQuote
(@sid-genetry-solar)
Member Admin
Joined: 4 years ago
Posts: 2890
 
Posted by: @dickson
PJ on ebay say not L1 N L2 . I know it can be wired L1 N L2 to the house but the 2 windings may not be balanced voltagewise . Is that the reason PJ say not L1 N L2 ?

I have always understood that warning to refer to the AC input--which can't handle a 3-wire AC input ("L1 N L2"), or the inverter will blow up due to a backfeed condition.

Beyond that, there is absolutely no issue with split-phase output from an "AMG transformer."  For that matter, there isn't any intrinsic design difference between the "5-wire" transformers and an "AMG 6-wire" transformer. 

 

Posted by: @dickson
IF jumper for direct 240vac single phase 60 hz and L1 and L2 not balanced is ok to start an inductive load but if wire split phase and a large load is on one of the 120vac line then the inductive load will not get the full 240vac output and may not start . That split phase may have an unbalanced line and reason to not L1 N L2 but wired as L1 and L2 direct to the well pump without neutral and ground connect to the inverter case .

Phase voltage imbalance is in most cases a complete non-issue--it's just the customer who notices it.  As most appliances accept a fairly large voltage range, it generally won't hurt or affect appliances in any way.

Most of the PJ inverters only regulate output voltage from a single 120v phase anyway--and often don't even have an AC output filter cap on the other phase.  This is even on the "5-wire" transformers, one of which I have on my bench right now.  The L2 wire goes directly from the transformer to the terminal block.  No filtering or regulation whatsoever on the other phase--and that's a v9.0 PJ inverter with a copper-wound transformer.

 


   
ReplyQuote
(@robertm)
Estimable Member
Joined: 3 years ago
Posts: 205
Topic starter  
On 1/24/2022 at 7:26 AM, Sid Genetry Solar said:

Can you provide a photo of the control board pot?

If there's 2 knobs, the other will adjust the internal battery voltage setpoints.  Differentiating is as simple as twisting one of them...if the output voltage doesn't change, put it back where it was, and twist the other one.

There's no science/rhyme or reason for the voltage adjustment...you'll just have to fire the inverter up with the cover off, and twist the knob while measuring the output voltage.

 

<fileStore.core_Attachment>/monthly_2022_01/IMG_20220126_113003_kindlephoto-1059454.jpg.f8fb9ff28f573696f1ffdca02c69e325.jpg

 😉Two pots, VR1 and VR2

 


   
ReplyQuote
(@robertm)
Estimable Member
Joined: 3 years ago
Posts: 205
Topic starter  
Posted by: @paul
Maybe I'm going a little off topic now, but whilst we are on the subject of wattages I noticed that the casing of your '8000w AMG' inverter looks more like the '6000w 230v' that they used to sell on ebay UK.

 

IMG_20220126_112936_kindlephoto-1229937.jpg


   
ReplyQuote
(@robertm)
Estimable Member
Joined: 3 years ago
Posts: 205
Topic starter  

LF-ASL2-AMG4


   
ReplyQuote
 Paul
(@paul)
Trusted Member
Joined: 3 years ago
Posts: 55
 

ASL2!? Thats even smaller than the one in my 8k 240v unit (ASL3). And my 8k unit can only do 3.5kW continuous.

But I notice they've changed the primary voltage from 18v to 16v, which should help reduce the flattened peaks on the sine wave under load.


   
ReplyQuote
(@robertm)
Estimable Member
Joined: 3 years ago
Posts: 205
Topic starter  
2 minutes ago, Paul said:

ASL2!? Thats even smaller than the one in my 8k 240v unit (ASL3). And my 8k unit can only do 3.5kW continuous.

But I notice they've changed the primary voltage from 18v to 16v, which should help reduce the flattened peaks on the sine wave under load.

From what little I understand, the chassis number may not be as important as the degree of copper windings?


   
ReplyQuote
(@sid-genetry-solar)
Member Admin
Joined: 4 years ago
Posts: 2890
 
Posted by: @paul
But I notice they've changed the primary voltage from 18v to 16v, which should help reduce the flattened peaks on the sine wave under load.

Copying Genetry Solar I see, haha 😉

It's hard for them to see my very detailed specification documents cross their desks without wanting to test some of the stuff themselves, haha.


   
ReplyQuote
(@sid-genetry-solar)
Member Admin
Joined: 4 years ago
Posts: 2890
 
13 minutes ago, RobertM said:

From what little I understand, the chassis number may not be as important as the degree of copper windings?

That would be correct. 

The "ASL2", "ASL3", etc., etc. are transformer core sizes (dimensions are PJ's own specification; these aren't standardized specifications).  A smaller core isn't necessarily a problem--except that it limits the amount of wire you can get around the core.  As far as I know, the wire (or lack thereof) is basically the limitation of the transformer's maximum wattage.

In theory, if wire had absolutely zero resistance, you could theoretically get an unlimited amount of power out of a very small core.

 

Curious how many strands the "battery" winding has?  I guarantee you the "output" windings will have a single strand of wire--and wouldn't be surprised if it isn't thin wire (i.e. 2.0mm diameter).


   
ReplyQuote
(@robertm)
Estimable Member
Joined: 3 years ago
Posts: 205
Topic starter  
Posted by: @sid-genetry-solar
That would be correct.

I measure the copper wire at 3mm.


   
ReplyQuote