PowerJack 30000Watt 48volt LF SP PSW 2 box inverter 2021 model 189 pounds

365 Posts
9 Users
1 Likes
4,244 Views
pilgrimvalley
(@pilgrimvalley)
Prominent Member
Joined: 4 years ago
Posts: 826
Topic starter  
Posted by: @dickson
4/0 Welding Cable carries 310 Amps for 600 volt in-line applications and that is not going to work . Two 4/0 welding cables in parallel is needed to be safe from fire .

that might be why the powerjack had the four connections for the inverter to battery connections on their large inverters....

but the gs12k down sized them to one post for positive and one post for dc battery cable connections....


   
ReplyQuote
(@dickson)
Noble Member
Joined: 4 years ago
Posts: 1058
 

but the gs12k down sized them to one post for positive and one post for dc battery cable connections..

I  think now that the GS12lw  can not be set to shut down at 16kw continuous .     The cable  inside the inverter is 4/0  or 3  or more  cables  equal to  4/0  rated   so the shut down  is 13000 watts to be safe .   One post mean one 4./0  cable  per post .                      if two 4/0 cables were used then a 400 amp fuse would need to be installed on each 4/0 cable....to be code legal....or would the fuse be required to slightly smaller??           NO  400 amp fuse on each cable .    IF 16KW  then  370 amps need  two  4/0 cable  at  310 amps each  but  one  400 amp fuse .   I  say 4/0 cable  but  two 3/0 cables also work with one 400 A fuse .     For 20kw shut down then  two  4/0 cable and one  500 amp fuse  .    


   
ReplyQuote
(@dickson)
Noble Member
Joined: 4 years ago
Posts: 1058
 

very few places get into the NEC DC fuse or DC breaker requirements of inverter cables....need more study/research

ALT E   chart      explain their way of using  BOTH   fuse  and  circuit breaker to protect   inverter and wire at the  same time     The  5500  inverter  will use a 250A breaker  to protect the inverter  AND  a  400A fuse to protect the 4/0 wire .    For  a 12kw  inverter running  12000 watts continuous  then  a 400A  breaker  to protect the inverter and a  400A fuse  to protect the one  4/0 wires     IF  16kw continuous  then  one 400A  fuse to protect the two parallel  4/0 wires .    All  PJ inverter has   glass fuse (40A)  or breaker 80A  to protect their inverter  and I  use 400A fuse to protect each of my  battery   (a lot of fuses )   

Screenshot (630766).png


   
ReplyQuote
(@dickson)
Noble Member
Joined: 4 years ago
Posts: 1058
 

but the again a non UL approved inverter will not likely pass an electrical inspection in most places in the USA...and may void your house insurance also???? better put it outside in a cement/steel fireproof enclosure...

The new  PV code  require UL listing for all grid-tie  inverter and  any  inverter for city permit .    I think Sean say PV permit may cost  1500 dollars to get permit approval  and then  another 1500 for inspection .    Engineering 775  say the inspector do not know what to look  so Engineering 775 turn on the system and that is ok  and pass and probably the city make an easy 1500 dollars .       Another youtube  show the stupid homeowner admit he overcharged the lithium-ion battery  in his living room on  home security camera .   The whole house burn down and insurance do not pay so he ask for donation on youtube .     I  think the insurance would pay if  he did not show how stupid he was  by overcharging the battery .    


   
ReplyQuote
pilgrimvalley
(@pilgrimvalley)
Prominent Member
Joined: 4 years ago
Posts: 826
Topic starter  

altE biggest DC breaker was only 250 amps so back to class t fuses. i have no dc breakers larger than 63 amps.

and only use the 400 amp class t fuses between the inverter and battery.


   
ReplyQuote
(@dickson)
Noble Member
Joined: 4 years ago
Posts: 1058
 

altE site says 400 amp dc fuse for 185 amp draw using a 5500 watt 48 volt inverter with 4/0 copper inverter cables

The 400 amps dc fuse is to protect the 4/0 cable .                     you can use a smaller DC  rated fuse/ DC rated breaker but then they may blow sooner to protect the 4/0 wire at less than 310 amps .    NO  the 250A breaker is not to protect the 4/0  wire at less than 310 amps but it is use to protect the inverter  and then can be reset again  like if you drop a long wrench  between the  2 inverter  posts  and short circuit  .       if it (the inverter) shuts down at 12000 watts then 12000 divided by 53 volts is only 226 amps   so the  breaker  will not trip  right away  .     That is ALT E  way to protect  inverter and  wires .       


   
ReplyQuote
pilgrimvalley
(@pilgrimvalley)
Prominent Member
Joined: 4 years ago
Posts: 826
Topic starter  

my concern was inadequately sized copper cable and overcurrent protective device (fusing or breakers) between the inverter and battery if the inverter was allowed to pull 18000 to 20000 watts from the battery...

altE table was for a 5500 watt inverter....so a lot smaller amp draw from a 48 volt battery...

Sean showed some breakers in a previous video but they were not actually hooked up....

most insurance companies look for an excuse not to pay up.... blame the stupid homeowner or someone else for bad wiring....perhaps

 

 


   
ReplyQuote
pilgrimvalley
(@pilgrimvalley)
Prominent Member
Joined: 4 years ago
Posts: 826
Topic starter  

Sean shows a 200 amp and 400 amp breaker but not showing any actually connected to the 12k prototype...

but sounds like he (Sean)maybe using 2/0 cable in the video below (2/0 cable is too small for 12k) (I may need to review/clarify that again ( Sean's statement) so don't quote that please...)

he SAID he bought some discontinued ones he said would cost 300 to 500 dollars each....

another huge cost to the 48 volt 12k system design.....

I bought the 400 amp class t fuses for 8.50 each and the class t fuse holder were about 30 dollars or so... will likely cost more today though...with inflation  🤔🤔🤔

I have spares but have never blown a 400 amp class T fuse (knock on wood).

 


   
ReplyQuote
pilgrimvalley
(@pilgrimvalley)
Prominent Member
Joined: 4 years ago
Posts: 826
Topic starter  

out of curiosity: I did find a 400 amp Heinemann 160 volt dc breaker new for $149 plus shipping on eBay and used/reconditioned for about 90 dollars,,,,but think the main purpose was a safety disconnect switch so still one would need an enclosure to mount it in as DC arc flash would be necessary to control.

I put in a battery disconnect switch for about 40 dollars on my 15k inverter,,,,

the problems i encounter are finding equipment that is suitable at high amperage at 48-volt DC and above...

looks like that 400 amp Heinemann breaker would require insulated stand offs mounted in a suitable enclosure....

400 amp safety switches dc rated are spendy....for sure....🤔


   
ReplyQuote
pilgrimvalley
(@pilgrimvalley)
Prominent Member
Joined: 4 years ago
Posts: 826
Topic starter  
Posted by: @pilgrimvalley
Sean shows a 200 amp and 400 amp breaker but not showing any actually connected to the 12k prototype...

yes he (Sean) in his YouTube video does say 2/0 wire is what he uses between the battery and 12k prototype,,,, so IMO and ampacity tables it say 2/0 copper cable is only rated at :

google search:

2/0 Gauge (AWG) Battery Cable is designed for higher amperage applications with a maximum voltage rating of 60 volts DC. 2/0 battery cable can comfortably handle 200 amps at a cable length of 15 feet.

so a 12k inverter would need more than 2/0 wire....the 400 amp breaker will not protect the wire at all when maxing out the gs12k inverter at 15000 or 18000 watts...

the 400 amp breaker will not trip and the wire will overheat with the pouch cell batteries at high amp draws...

15000 divided by 53 volts equals 283 amps

18000 divided by 53 volts equals 339.62 amps 

the Heinemann 400 amp 65 volt dc rated breaker is only acting as a switch with the wrong over current rating needed for 2/0 copper cable..

the NEC code allows 175 amps for 2/0 copper cable and up to 195 amps for 2/0 cable if you buy the higher prices specialized cables...that have the more expensive insulative jacket...

you should review and reply 🤔🤔

they would likely red tag your house....if they find out....etc

but then again I am not the electrical inspector or utility company representative,  or a engineer or electrician....

have a safe Monday 😎 and all other days for that matter!!!


   
ReplyQuote
pilgrimvalley
(@pilgrimvalley)
Prominent Member
Joined: 4 years ago
Posts: 826
Topic starter  

I bought 100 amp and 200 amp disconnects the last 3 years.... the 200 amp ones were at least twice the price as the 100 amp ones, and it looks like the 400 amp ones are about twice the price as the 200 amp ones...

I hate working around live wires about as much as I hate working with plumbing under pressure....so valves and disconnects are a big priority for me...🤔🤔🤔😎😎😎

they need a good engineer/electrician to chime in to their forum....

 


   
ReplyQuote
(@sid-genetry-solar)
Member Admin
Joined: 4 years ago
Posts: 2890
 
20 minutes ago, pilgrimvalley said:

they need a good engineer/electrician to chime in to their forum....

I've pretty well written this thread off as something to ignore; there's just so many unverified wild assumptions being stated as reality that it's simply not worth my time to refute every new message that comes up.  I can't get anything else done if I'm always trying to keep things straight here.

 

Sean's battery cables on the 12kw GS inverter are 4/0.  I have absolutely no idea where the "Sean's battery wires are 2/0" assertion came from...unless someone can provide a YT video link to prove the statement.  The only reason he isn't using heavier wire is because I don't think he knows that bigger than 4/0 is measured in MCM sizes...

...heck, for the longest time, he had TWO 4/0 battery wires on each terminal (one from each battery module).

 

3 hours ago, pilgrimvalley said:

out of curiosity: I did find a 400 amp Heinemann 160 volt dc breaker new for $149 plus shipping on eBay and used/reconditioned for about 90 dollars,,,,but think the main purpose was a safety disconnect switch so still one would need an enclosure to mount it in as DC arc flash would be necessary to control.

Again, I have absolutely no idea where the assumption here comes from.  They're a breaker, and they're rated to safely disconnect a load at up to (depending on the breaker) 10,000AIC (amps interrupt current) at the rated voltage.  Got the breaker?  You don't need any other switches.

 

But I digress.  I need to actually get stuff done.


   
ReplyQuote
(@dickson)
Noble Member
Joined: 4 years ago
Posts: 1058
 

I hate working around live wires about as much as I hate working with plumbing under pressure....so valves and disconnects are a big priority for me...🤔🤔🤔😎😎😎

When I was living  in IOWA  a rich farmer I  know  instead of hiring  someone to work on his well  pump    he unscrew  the plug  under high  pressure and it  hit him between his   eye  and was kill  instantly  .      Most engineer I  know will pay  someone  to do electrical  works  and be safe  .      


   
ReplyQuote
pilgrimvalley
(@pilgrimvalley)
Prominent Member
Joined: 4 years ago
Posts: 826
Topic starter  

https://youtu.be/zHaXeEgbrnc

Posted by: @sid-genetry-solar
Sean's battery cables on the 12kw GS inverter are 4/0. I have absolutely no idea where the "Sean's battery wires are 2/0" assertion came from...unless someone can provide a YT video link to prove the statement.

in the above YouTube video the Genetry Solar 12k inverter is using 2/0 welding cable according to Sean's clearly worded and repeated statement....he is using the wrong size inverter cabling... at 12:19 in the video....he claims the 2/0 cabling use....watch it when you have the time....

in his later video the gs12k prototype inverter was running up to 18000 watts before it shut down to protect the mosfets....obviously the breaker was not protecting the 2/0 cable he repeatedly said he used.....in the above video...

but then again he (Sean) does not actually show any real/actual cable and breaker connections only shows a large breakers that are not connected... he said they cost him $100 each for the 400 amp DC breaker 65 volt rated...(Heinemann brand).

review his video... i watched it Sean's YouTube video twice and he clearly says he is using 2/0 inverter cabling.

a 400 amp breaker will not protect a 2/0 wire as the wire will overheat,,,, but then again maybe Sean needs to make a corrected YouTube video if he is publishing the wrong information about his prototype gs12k inverter sizing....

the 400 amp breaker will not trip until the 2/0 wire is way past is NEC (national electric code) allowable ampacity rating.....

he is using it a a disconnect switch and it will have the wrong size for 2/0 cables that Sean says he used...the breaker sizing's purpose should be to protect the wire from fire....that is why the NEC code lists the 2/0 cable to 175 or 195 amps maximum is to prevent the wire overheating and being the weak link potentially causing a fire...

a DC rated disconnect switch for 400 amps is expensive....anything above 200 amps is expensive... i have purchased them in the 100 and 200 amp sizes.....

he does not show them actually connected and so perhaps he does not know the actual cable size....

A side note: I had to replace a water valve under pressure in the city as the city's curbside water shut off did not function, and the small city would not repair their curbside water shut off valve...

A simple battery disconnect switch can be installed for 30-40 dollars....

the breaker with the correct size batter cable rating would be useful....I use class T 400 amp fuses with 4/0 copper cable plus the simple battery disconnect switch....the class T fuse have a 20,000 AIC (amps interrupt current) rating which I like better for the LiFePO4 banks I have assembled...

have a safe and productive day and never believe all the things you see...in YouTube videos🤔🤔

Biden makes gaffes routinely but he is 70 plus years old....🤣🤣🤔🤔😎 perhaps 78 to 79 years old today( i did not look it up)

assuming is never anything more than a guess and as often than not is the incorrect conclusion....😢

 

 

 

 

 


   
ReplyQuote
pilgrimvalley
(@pilgrimvalley)
Prominent Member
Joined: 4 years ago
Posts: 826
Topic starter  
Posted by: @dickson
Most engineer I know will pay someone to do electrical works and be safe .

maybe Sean needs to hire an electrician like Engineer775 routinely does in his YouTube videos...👍

the Canadian engineer I follow gives good practical advice....

my freshman college year (in The Towers Dorm)   >>>>my friend was an engineer....he was from my hometown and we worked in the soybean fields hoeing out the weeds together...freshman were required to live on campus as I recall...

I was a chemistry major and animal science major....

good licensed electricians usually have all the best safety equipment....i am always buying better tools it seems...🤔


   