As it appears that the inverter runs with nothing connected to it, the issue likely has to do with the way the inverter is connected to the breaker panel and/or possible ground-neutral bonding problems.
The rev 11.3 control board is working frrom your video and you measure 114vac from L2 to G . Do not use the AC 110 INPUT for charging . The yellow ground is like on my control board and the N and the L1 to your control board is correct like mine . I do not have charger connected so can not tell if your charger wiring is correct . Connect direct to L1 N should work and connect direct to L2 N should work without breaker panel .
surprisingly the single receptacle wired as L1 +L2 and chassis ground working without tripping the breakers.
NOT surprising because the recptacle bypass all wiring to the charger board . Receptacle L2 is direct to the transformer and L1 is from control board and transformer . Transformer wiring is correct and control board is working with 3 LED on green steady .
Lots of great informations , thank you. I will be using this unit as lone inverter using a charge controller for my batteries.
Thanks again
Shame, that AMG looks exactly like mine. Never had a lick of issues with it aside from less-than-stellar voltage regulation.
Honestly it sounds like something is wrong with how it's wired to the panel. Have you tried unwiring it from everything except your DC bus and just testing the AC receptacle?
Skip the ground and try some light loads, then some heavier ones if that works.
NotMario,
I myself thought the issue was related to ground as well, after testing the theory the results unchanged. Using the same exact household load setting in use for the single AC receptacle “ currently working fine “ but ( sparks from hardwired blocks ) I give up trying on this……
Note ….now I have tried this with caution , power conditioning and surge protection completely away from the house and the sub panel from my other system I am able to power some appliances but those protections indicated ground fault.
by the way is it normal for the ongoing humming with or without load or AC input?
<a href="/monthly_2022_12/CF4422F4-71D3-495A-81C4-402692BB2669.jpeg.ccf41e70c27c3261909bf54b17f90caf.jpeg" class="ipsAttachLink ipsAttachLink_image" ><img data-fileid="2003" src="//forums.genetrysolar.com/applications/core/interface/js/spacer.png" data-src="/monthly_2022_12/CF4422F4-71D3-495A-81C4-402692BB2669.thumb.jpeg.4e75996e10d22d9db694d94149965397.jpeg" data-ratio="133.45" width="562" class="ipsImage ipsImage_thumbnailed" alt="CF4422F4-71D3-495A-81C4-402692BB2669.jpeg">
by the way is it normal for the ongoing humming with or without load or AC input?
It's a PJ...so yes, a constant hum from the transformer is normal. (A GS inverter will be practically dead silent at no load as a result of the perfectly matched FET drive.)
No load current on the DC side should be at or under 1A if you have some way of measuring that. (Clamp meters that can measure DC current are invaluable in any sort of off-grid system! FWIW most cheap clamp meters can only measure AC current.)
I myself thought the issue was related to ground as well, after testing the theory the results unchanged. Using the same exact household load setting in use for the single AC receptacle “ currently working fine “ but ( sparks from hardwired blocks ) I give up trying on this……
We've already kinda established that grounding is messed up.
If you ignore inverter chassis ground, and only connect the Line and Neutral lines, you should not have any problems.
Of course if the wires are swapped, trying to connect this inverter to a breaker panel will result in sparks and tripped breakers--because of ground-neutral bonding. It's highly likely that due to the not-isolated-ground problem, you're shorting the inverter out with a breaker panel--which will bond ground and neutral together. Betcha "inverter case ground" is shorted to the AC output line you're considering "hot"--so shorting "ground" and "neutral" together deadshorts the output of the inverter.
A GS inverter will be practically dead silent at no load as a result of the perfectly matched FET drive.)
Are these FET drive compatible with PJ 12000 AGM?
A month of sleepless nights trying to understand the mystery , although I called it uncle…. this AM before hitting the road I was at it
I took off the ground completely out of the unit to my disappointment result was not changes, but I discovered something interesting that the AC input L has continuity with the chassis, I do not know all fundamentals about electricity but I repair equipment., Am I wrong to say those input wires (L with chassis continuity N no continuity )are crossed?
A GS inverter will be practically dead silent at no load as a result of the perfectly matched FET drive.) Are these FET drive compatible with PJ 12000 AGM?
GS control boards only have a single FET board output connector, not a double like PJ does. In addition, the PJ FET boards would need either modified with the addition of a zener diode to each one (to prevent FET failure due to the stronger drive) and/or outright replacement with a set of GS LegacyFET boards (best case).
Due to the design limitations of a PJ mainboard, you would not be able to exceed much over 6kw output with a GS setup. But there's also no way the "12000W AGM" transformer will be able to do 6kw continuous in the first place.
A month of sleepless nights trying to understand the mystery , although I called it uncle…. this AM before hitting the road I was at it I took off the ground completely out of the unit to my disappointment result was not changes, but I discovered something interesting that the AC input L has continuity with the chassis, I do not know all fundamentals about electricity but I repair equipment., Am I wrong to say those input wires (L with chassis continuity N no continuity )are crossed?
You might have honed in on at least one of the issues 😉.
None of the AC input or output leads (nor the DC input leads) on the inverter should be short-circuited to the chassis.
The lowest connection between any terminal and the chassis should be >1 Megohm.
I am not sure if this is an isolated incident, I have had a lot of issues tripping breakers blew up Fetts and so on with my 12000 watt AGM, after taking the unit apart many times tracing wiring , I discovered some of the wires were crossed (output) after fixing these issues the machine has been working for quite awhile without any problem crossing my fingers. Unfortunately there’s no manual for reference..!I been running the living room area TV and satellite devices and a small deep “freezer at night “with a power transfer of course I don’t want to peeve my queen when she is watching TV.