48 minutes ago, Glenn S said:Is the process similar to this vid?
Can't say it is. On the larger PJ boards, the L2 transformer wire went to the PCB--which is what Sean was connecting to in this video (brief click-through, didn't watch it). On your inverter, the L2 transformer wire goes directly to the front panel (not the PCB)--so you might even consider putting an external cap from L2 - N on the front panel.
49 minutes ago, Glenn S said:Also, I never did find that led4 on this v11 board. I'm assuming they've deleted it, but if Sid or anyone else has seen it, please let me know where so I can remove it.
Well, I think it's in the same place--photos obviously are lower resolution here, but I found an LED in the exact place of LED4 on a 10.3 control board (yellow circle) in a photo you posted on this thread:
<fileStore.core_Attachment>/monthly_2021_07/image.png.cb40ac75d087709c702d5cef6bf96524.png
You could try to desolder the LED--or you could brute-force it like I did, and just twist the LED off the board with some needlenose pliers. Either way, check very carefully to make sure the pads aren't shorted when you're done. Might quiet the inverter down a tad.
Blue circle: if you want a "donor cap" you can pop one of these off.
I do notice that the terminology on the board says "L2" instead of L1...whatever. You want this cap to go from the transformer neutral wire, to the phase that goes unfiltered directly to the front panel.
52 minutes ago, Glenn S said:Having the over heating issues that so many do, so I've ordered another delta fan. It's a 24v fan so I'll run it straight off the inputs so as not to ask anything more of the control board. I've put a hole in the top, right over the tranny, and a hole beneath it as well as removed the retainer. This will allow me to force a shit ton of air through the toroid and should eliminate that problem forever. I've come up with a new retainer that will hold the transformer in place from the outside rather than going through the middle and covering the hole.
Well, I'll wish you best of luck with trying to stop the overheating 😉. Tried a mod on my "9kw" PJ inverter: had the toroid mounted upright, with a 200CFM Delta blowing directly through the center of the donut. Still overheated at 3kw...
...solution was to get a transformer wound for better spec!
I recently ohmed out an ASL9 transformer used in a "20kw" PJ, and calculated the losses at 20kw at 2,146W of heat in the transformer. 1,472W of that was the secondary alone. Nope, that level of heat dissipation isn't possible...not unless it's submerged in liquid moon juice.
Is the process similar to this vid?
Be careful of doing what the old video show . The video show the old output charger board . I have the new output board 10.1 and the picture . L2 is the wire that need to be filter as Sid said . I am changing the parts on my 15kw PJ inverter and am surprise at what I find out and will post later .
I think it's in the same place--photos obviously are lower resolution here, but I found an LED in the exact place of LED4 on a 10.3 control board (yellow circle)
My rev 11.1 control board has 4 LED and in the same place as the 10.3 board . The LED (circle yellow) do no light when the inverter is running and working as in my picture The LED (circle yellow) will light when there is an error and the inverter will not start or if running the Led (circle yellow) show that the inverter will shut down soon or the mosfetts will blow up soon which happen to me many times . Sid is right that the rev 11.1 board is the same and the connection is the same as the 10.3 board . The difference is the short mainboard ribbon cable is twisted and shield that connect to the original mainboard . The rev 11.1 control board works good as a replacement for older powerjack .
5 minutes ago, dickson said:My rev 11.1 control board has 4 LED and in the same place as the 10.3 board . The LED (circle yellow) do no light when the inverter is running and working as in my picture The LED (circle yellow) will light when there is an error and the inverter will not start or if running the Led (circle yellow) show that the inverter will shut down soon or the mosfetts will blow up soon which happen to me many times .
The LED I put a yellow circle around on the photo taken by @glenn-s...is already missing from your control board, see circled area below:
<fileStore.core_Attachment>/monthly_2021_07/image.png.a824f7f869bc64a2131f77ff57dcfd44.png
The LED I put a yellow circle around on the photo taken by <a contenteditable="false" data-ipshover="" data-ipshover-target="/profile/69-glenn-s/?do=hovercard" data-mentionid="69" href="/profile/69-glenn-s/" rel="" style="font-size:12.6px;padding:.1em .8em;">@Glenn S...is already missing from your control board, see circled area
You are right . I look at my rev11.1 board with a magnifly glass and the LED is not there but is on the rev10.3 control board . That LED light and blink when rev 10.3 has error . I have your LF Driver Board rev 1.0 and will test before using to see if it will blow out FETS . Blowing 24 FETS on one mainboard is 100 dollars .
I have your LF Driver Board rev 1.0 and will test before using to see if it will blow out FETS .
The new LF Driver design I provided to PJ is not affected by the LED4.
Reportedly it causes smoke at higher loads, but is fine at lower loads. 2 possibilities that I'm aware of right off:
- ring in the ribbon cable (which has a terrible pinout) punching the FET gates out (can be helped with 15v zener on the MOS boards)
- crosstalk due to poor mainboard layout causing extreme FET heat/burn
I am not sure why the PJ LF driver being very imbalanced somehow does not have this problem.
I am not sure why the PJ LF driver being very imbalanced somehow does not have this problem
PJ LF driver do have this problem on 15kw 20kw 25kw 30kw and even worst . The FETS all blow out and the resisters on mosboard are bad and I can not rebuild the mosboard with new FETS . Sometimes the control board need to be replace . It will take me a while to make a test bench for testing FETS at 60v and your LF driver or PJ LF driver at 60v before using . Powerjack may modify your LF driver and is selling it . If powerjack is not broken do not try to fix it or it just get worst and more expensive .
Powerjack may modify your LF driver and is selling it .
Thus far, they haven't modified it. I really could care less if they hock it--I gave the design to them to do with as they chose.
This will allow me to force a shit ton of air through the toroid and should eliminate that problem forever. I've come up with a new retainer that will hold the transformer in place from the outside rather than going through the middle and covering the hole.
IF you not going to move the inverter then leave the rubber pad off and have no retainer bracket at all . I remove the pad and the retainer and my 15kw ASL9 transformer never go over 150 degree F now and would not auto shut down at 170 F degree like before I stlii shut down manually when battery voltage drop to 50 v . My heat pump do not like square wave .
IF you not going to move the inverter then leave the rubber pad off and have no retainer bracket at all . I remove the pad and the retainer and my 15kw ASL9 transformer never go over 150 degree F now and would not auto shut down at 170 F degree like before I stlii shut down manually when battery voltage drop to 50 v . My heat pump do not like square wave .
Actually I'll be flipping it and mounting it upside down. New bracket was necessary,😃
Quick update, thank you Sid, for pointing that led4 out for me. No wonder I couldn't find it. It has been deleted from the v11 boards apparently.
I'll do the cap this coming weekend, as this last one was a holiday so I was out camping.
Why on earth do they have l1 going to the l2 location on the board? That has to be frustrating for the ones building it even, no? If I'm building inverters and I see that every board is labeled incorrectly, that would drive me nuts lol ☺
I stlii shut down manually when battery voltage drop to 50 v . My heat pump do not like square wave .
Mathematically, the minimum battery voltage your inverter can take and still provide a sine wave--at no load--is 53.125v, assuming 240v output. Under any load, this number will increase.
Those are probably standard 5x20mm fuses. If you have a ruler that has mm on it just check that way and see if it comes out right. then you know what to buy. I can get most sizes of fuse locally but you may have to order online. I would recommend replacing the glass fuses with ceramic fuses to reduce the chance of rupture but other than that either type should get the job done.
Those are probably standard 5x20mm fuses. If you have a ruler that has mm on it just check that way and see if it comes out right. then you know what to buy. I can get most sizes of fuse locally but you may have to order online. I would recommend replacing the glass fuses with ceramic fuses to reduce the chance of rupture but other than that either type should get the job done.
Thanks. Since I don't use the front outlets, I bypassed them altogether and wired it direct.